How to calibrate flow transmitter for Capillary type


How to calibrate flow transmitter for Capillary type

flow_differential_pressure_capillary_type

Material
Data sheet
Pressure calibrator (std)
Multimeter (std)
Hart communicator

Step
*Ask panel man to put the controller in manual mode for control loop and to put it on MOS for ESD loop.
*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process..
*Open vent valve at drip ring and open plug at the top of the drip ring (if available) to release the process pressure
*Clean the liquid inside the drip ring and put back the plug for high side only (if available).
*Connect pressure calibrator to high side of manifold
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*Apply pressure as per data sheet LRV (normally 0mmH2O)
Multimeter should show 4mA
If not, do zero adjustment at transmitter using HART Communicator
*Apply pressure as per data sheet URV
Multimeter should show 20mA
If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)
*After completion of the job ask panel operator to put loops back in normal mode or normalize the MOS
*Fill the calibration form and file it for future reference.

Example calculation
Instrument calibrated range: 0 – 2500 mmH2O
Process calibrated range: 0 – 130 m3/h
Q =K  P
0%  0 mmH2O = ( 0/2500) x 130
= 0 m3/h 
50%  1250 mmH2O = ( 1250/2500) x 130
= 91.9 m3/h 
100%  2500 mmH2O = ( 2500/2500) x 130
= 130 m3/h







Share on Google Plus

About denizen robo

This is a short description in the author block about the author. You edit it by entering text in the "Biographical Info" field in the user admin panel.
    Blogger Comment
    Facebook Comment

1 comments:

  1. The principle of Capillary type flow transmitter based on heat transfer and the 1st law of thermodynamics. During the process the flow of gas divided into two paths when it enters to the flow instrument. The majority of gas flows through Laminar Flow Elements bypass and a small amount of gas passes through the Capillary Sensor tube with an ID.