Calibration Procedure:

*Hook up HART Communicator and verify some parameters by refer to data sheet. Typical parameters are, tag number, PV, LRV and URV.
*Isolate the instrument from the process.
*Remove connection at manifold to the process after release the process pressure
*Connect pressure calibrator to high side of manifold
*Expose the low side to atmosphere
*Hook up a multimeter in series with the signal to the DCS to measure current signal.
*Apply pressure as per data sheet LRV
Multimeter should show 4mA
If not, do zero adjustment at transmitter using HART Communicator
*Apply pressure as per data sheet URV
Multimeter should show 20mA
If not, do span adjustment at transmitter using HART Communicator
*Verify the linearity by increasing and decreasing the pressure (0%,25%,50%,75%,100%,75%,50%,25% and 0%of range)


Note
LRV and URV range from data sheet should include the pressure effect from bottom flange height to the transmitter and the SG of process liquid.

Example calculation
S.G=0.89
A= 2000mm (measurement length)
B= 100mm (off set)
C=A+B=2100mm
Dp = pressure at high side – pressure at low side
LRV    = (B x S.G) – pressure at low side
    = (100mm x 0.89) – 0
    = 89 mmH2O
URV     = (C x S.G) – pressure at low side
    = (2100mm x 0.89) – 0
    = 1869 mmH2O

Related posts:
Displacer level transmitter calibration and installation consideration
Capillary type DP level transmitter
Flow transmitter pitot type calculation and calibration
DP Flow transmitter calculation and calibration.
Share on Google Plus

About denizen robo

This is a short description in the author block about the author. You edit it by entering text in the "Biographical Info" field in the user admin panel.
    Blogger Comment
    Facebook Comment

1 comments: